I recently purchased an Apex 300 and am working on the optimum Solar Panels for this model. If i understand correctly, there are 2 solar inputs and each input is rated 60v max @ 10 A. Since i am in a cold climate, i needed to calculate the Voc for -40 C which is likely colder than i might need but there may be a remote chance it could drop to -40 C.
I used an Excel Spreadsheet to calculate the Voc for various panels and found that the JA Solar model JAM60D41-510/LB seemed to provide the best results. Other panels had a Voc that seemed close to 60v but i would like a safety margin on the voltage of maybe 7 or 8v.
The specs for the JA Solar panel are:
Pmax=510w
Voc=44.25v
Vmp=37.31v
Imp=13.67A
Voc temperature Coefficient=-0.25% / Deg C
I calculated a worst case Voc @-40 C as follows:
25 C - -40 C = 65 C temperature change
-0.25% * 65 C = 16.25% per 65 C change
16.25% of 44.25 = 7.19v change in Voc
So worst case Voc (@ -40 C) would be 44.25v + 7.19v = 51.44v
Max power generation would be 37.31v x 10A (ma clamped at 10A) = 373.1w * 2 Panels * 2 inputs = 1492 Watts.
Do these calculations seem correct ?
Will there be any issue with the Apex 300 being able to clamp the 13.67A to 10A without causing overheating ?
Is my safety margin of 7 or 8v too excessive ? Some panels generate a worst case Voc of 58.4 but have the ability of producing about 1678 Watts.
Thanks