We recently installed the Bluetti EP760 system in a private home, but we’re encountering an issue with charging from a generator. We’ve tried various generator models, including the Matari MH11000EA-ATS and a smaller inverter generator, but none of them seem to work.
When we connect the generator to the house without the EP760, everything operates normally. However, once the EP760 is in the setup between the generator and the power consumers, we encounter problems. The EP760 displays error messages such as “voltage too high,” “voltage too low,” and “frequency voltage too high/low.”
The EP760 works perfectly in off-grid mode and functions well when grid-connected, charging properly and supplying power during grid outages. The manual for the EP760 doesn’t mention specific issues related to generator connections.
Could anyone offer advice on what might be causing this issue and if there is a way to resolve it so that the EP760 can charge from the generator?
There are 2 types of inverters. Modified sine wave and pure sine wave. A modified sine wave is cheaper to produce but also less effective and maintaining a smooth frequency, its actually kind of coarse and choppy. Most household items will run just fine on a modified sine inverter but electronics and charging bricks don’t work well with them. Pure sine inverters create a true “pure” sine wave and are preferred but also more expensive. I can’t say for sure but it’s possible your generator has a modified sine inverter, and the charging brick will not work with it.
Hi @Max13, I agree with @doecliff’s opinion, maybe it is the generator does not output pure sine wave.
To resolve this issue, we recommend updating all firmware to the latest version. Then, go to Advanced Settings and enable Generator Mode. This will help the EP760 adapt to a wider range of voltage inputs. Please let us know if it does help.
Hi @doecliff and @BLUETTI_CARE , thanks a lot for input!
We really had outdated firmware and didn’t have Generator button. We got it after update, but still both generators didn’t work, despite both of them pretend to give pure sine (that’s why the smaller one is called “inverter” generator) and both of them work well with sensitive electronics requiring pure sine - consumers like heating system pumps, fridge etc.
EP760 shows the same mistakes B098, B099, B100.
However we tried another generator and it worked well - this one GENERGY LIMITED 2000i Buy Gasoline generator GENERGY LIMITED 2000i (nom 1.7 kW, max 2.5 kVA) GENERGY-LIMITED-2000i in the online store Генераторы ЭТС Энерджи
Now we have to find the way how to clean the sine from the Matari generator.
Thanks again for input!
Hi @Max13, If other generators are working fine, it suggests that this generator has significant voltage and frequency fluctuations, which may be causing the charging issue.
We recommend that you log into the Bluetti app, connect the generator, and check the voltage and frequency readings.
This will help us investigate the problem further.
UPD: Problem solved, received latest update for EP600 parallel connection and now works great
Same problem, I guess Bluetti have a lots of bugs in firmware.
EP6002 + 8b500 setup, generator 33kVa (27kW) professional high quality - Perkins, not charging from generator at all.
Tried generator button, tried enable grid self adaptation, tried all authentication settings, but problem exists.
Current voltage readings
L1: 227.7 Freq: 50.9
L2 230.9 Freq: 50.9
L3: 231.2 Freq: 50.9
Hi @Olvrick thank you for sharing information! Did you get firmware update through the app or by request from Bluetti? Just to understand whether we have a chance to solve our problem in the future.