The Apex300 is rated for 3840w continuous and 7680w peak. I want to get more info on how long it can handle various peak loads for. Especially for starting AC and fridges. For example, how long can it handle 5760w or 7680w for?
1.05 times < load power < 1.2 times: 2 minutes
1.2 times < load power < 1.5 times: 10 seconds
1.5 times < load power < 2 times: 0.5 seconds
@snowstorm Please refer to the above, which is calculated based on the rated maximum output power.
Thanks. If one connects 2x Apex300 together using an A1 hub, would this be doubled?
My question pertains to running a central AC unit. Specifically the 3 ton model of the https://s7d2.scene7.com/is/content/AlliedAirEnterprises/1%20-%20Document%20Updates/FLAGSHIP_AIRCONDITIONERS_4SCU14LB-OMNIGUARD_SPECSHEET.pdf
When running, this uses around 2200w, but I know the startup surge would be much higher.
How many Apex300 in parallel would be require to start and run this?
The Locked Rotor Amp is 79A, at 240V, that would be nearly 19kW, which seems crazy high.
Yes, Output power can be doubled to 7,680W.
However, the start-up power of your air conditioner may reach 5-7 times the rated power, so two Apex300 units may not be able to handle.
What is recommended to start a 3 ton central AC unit? What have you guys seen in your testing?
The team has only tested one AC in the lab: two Apex300 units in parallel can support a Gree 30,000 BTU air conditioner with no issues.