I have a split phase setup.
I want to charge the batteries from a single 120V Honda generator when the utility power is out, even charging them one at a time, if I have to.
My plan is to purchase two T500 AC-DC chargers and plug one into each AC300. Each inverter will only see DC power and should have no knowledge or effects from the single phase 120V AC power source powering two T500s at the same time.
Not my favorite approach, but otherwise I would have to shut down both AC300, remove the communication cable, bring them back up in single phase mode (and re-cable to the generator) with the AC power output off. Reversing the procedure after the charging was complete and having no AC power during the charging.
Prone to mistakes and confusion at best.
It seems easier to charge them both at the same time with DC chargers.
It’s a shame it’s only 500W of charging, per AC300, at a time for the T500.
I assume that the 500W rating is the output power from the T500, not tthe input power.
Even at a 90% efficiency, that’s 556 watts consumed by each T500.
My little Honda EU2200i is rated at 1800W continuous, so a pair of T500 might consume around 1112W.
If I was sure that the power supplies were 90% efficient (never consumed more than 556 watts for the T500), I could use four T400 for an estimated 1778W total. That’s a bit too close to the 1800W continuous rating of the generator and it’s still my assumption that the power supply is 90% efficient.
I can’t find any technical specifications for the T500/T400 power supplies.
Other ideas worth considering?